I am polling a table of mixed data:
Agent Name | dataIntRegister |
dataIntName
| ObjectInstance
42.108.54.10 |
0
| Low Coolant Temp |
1
42.108.54.10 |
0
| High Coolant Temp |
2
42.108.54.10 |
0
| Low Oil Pressure |
3
42.108.54.10 |
0
| Generator Not In Auto |
4
42.108.54.10 |
0
| High Coolant Temp Trip |
5
42.108.54.10 |
0
| Low Oil Pressure Trip |
6
42.108.54.10 |
0
| Overcrank Trip |
7
42.108.54.10 |
0
| Overspeed Trip |
8
42.108.54.10 |
0
| EMCP Diagnostic Trip |
9
42.108.54.10 |
0 |
UPS On Battery
| 10
42.108.54.10 |
0
| UPS Summary Alarm |
11
42.108.54.10 |
0
| UPS CB1
Open |
12
42.108.54.10 |
0
| UPS CB2
Open | 13
42.108.54.10 |
0
| UPS CB3
Open |
14
42.108.54.10 |
0
| UPS Critical Bus OK |
15
42.108.54.10 |
0
| UPS Minor Alarm |
16
42.108.54.10 | 0 |
UPS Major Alarm |
17
42.108.54.10 |
0
| UPS Low Battery
| 18
42.108.54.10 |
0
| UPS AC Power Loss |
19
42.108.54.10 |
0
| A/C #6 Alarm |
20
42.108.54.10 |
0
| A/C #7
Alarm |
21
42.108.54.10 |
0
| Switchgear Utility Open |
22
42.108.54.10 |
0
| UPS on Maint Bypass |
23
42.108.54.10 |
0
| UPS Output Bkr Open |
24
42.108.54.11 |
0
| A/C #1
Alarm |
1
42.108.54.11 |
0 |
A/C #1 Moisture |
2
42.108.54.11 |
0
| A/C #2
Alarm |
3
42.108.54.11 |
0
| A/C #2 Moisture |
4
42.108.54.11 |
0
| A/C #3
Alarm |
5
42.108.54.11 |
0
| A/C #3 Moisture |
6
42.108.54.11 |
0
| A/C #4
Alarm |
7
42.108.54.11 |
0
| A/C #4 Moisture |
8
42.108.54.11 | 0 |
A/C #5 Alarm
| 9
42.108.54.11 |
0
| A/C #5 Moisture |
10
42.108.54.11 |
0
| Chiller Water Detector |
11
42.108.54.11 |
0
| PDU 1 Alarm |
19
42.108.54.11 |
0
| PDU 2
Alarm |
20
42.108.54.11 |
0
| PDU 3
Alarm |
21
42.108.54.11 |
0
| PDU 4
Alarm |
22
42.108.54.11 |
0
| PDU 5
Alarm |
23
42.108.54.11 |
0
| PDU 6
Alarm |
24
42.108.54.11 |
19
| Temperature #1 |
25
42.108.54.11 |
45
| Humidity
#1 |
26
42.108.54.11 |
22
| Temperature #2 |
27
42.108.54.11 |
40
| Humidity
#2 |
28
42.108.54.11 |
20
| Temperature #3 |
29
42.108.54.11 |
44
| Humidity
#3 |
30
As you can see it is a combination of temp, humidity
and state information.
The problem I am running into is I cannot create
multiple thresholds against this information. Netview is telling me I cannot collect
the same mib object again for the same node. I also cannot use the same
threshold for every item in the table.
Does anyone know how to get around this?
I need to threshold the following with the same thresholds.
42.108.54.10 |
24
| UPS room temperature |
25
42.108.54.11 |
19
| Temperature #1 |
25
42.108.54.11 |
22
| Temperature #2 |
27
42.108.54.11 |
20
| Temperature #3 |
29
42.108.54.11 |
45
| Humidity
#1 |
26
42.108.54.11 |
40
| Humidity
#2 |
28
42.108.54.11 |
44
| Humidity
#3 | 30
42.108.54.10 |
11
| UPS room humidity | 26
Everything else is a 1 or 0